10/2/15 12:20 p.m.

The parking pad discussion got me thinking. How do I figure out the strength of my existing slab? Thinking of putting up a hoist, but need 4,000 psi concrete. Floor was poured in the late 90's and looks good.

Duke
Duke MegaDork
10/2/15 12:26 p.m.

Find somebody with one of these. Search for "nondestructive testing" and inspections. Somebody should be able to help you out pretty easily.

xflowgolf
xflowgolf Dork
10/2/15 1:22 p.m.

Also interested to find out. Similar situation, considering hoist... house was built/poured around 1990. No idea on material specs.

Nick (Not-Stig) Comstock
Nick (Not-Stig) Comstock PowerDork
10/2/15 1:30 p.m.

If I'm not mistaken the code was changed to allow 2500 psi in the late nineties or early 2000's. Prior to that, at least where I'm from, minimum psi for flat work was 3500. Also keep in mind that concrete continues to harden for many years, meaning a twenty year old slab will test harder than a 30 day slab.

KyAllroad
KyAllroad SuperDork
10/2/15 1:30 p.m.

Core drill a non critical spot. Take core sample to geotechnical lab for destructive testing. They'll crush it and figure out the strength for you.

Generally concrete is speced to be 3,500 psi but since no supplier wants to have to replace substandard material they generally err on the side of stronger. When I tested concrete in the late '90s for a living 3,500 mix would test out around 4,000-4,300 at 28 days. YMMV

RX8driver
RX8driver New Reader
10/2/15 2:06 p.m.

The other thing to consider is how thick is the concrete?

SVreX
SVreX MegaDork
10/2/15 2:18 p.m.

Is the manufacturer's spec 4000#, or someone's opinion?

I've done several, and have never seen a manufacturer spec of 4000#. Some lifts require 6" thick concrete, but most seem to allow for 4" now.

If it needs 4000# 6", you probably don't have it. Buy a different lift.

4000# is pretty rare in residential.

Appleseed
Appleseed MegaDork
10/2/15 5:21 p.m.

Also rebar, it's size, and how it was laid out before pour, will affect the strength and stability of a slab.

secretariata
secretariata GRM+ Memberand Dork
10/3/15 12:29 a.m.

Sorry Duke, but Schmit Hammer's are always optimistic. That (plus the fact it is less $ than preparing specimens and performing a destructive compression test) is why contractors generally want to use it. Experienced owners specify a cylinder or core be compression tested instead.

Kenny_McCormic
Kenny_McCormic UltimaDork
10/3/15 1:13 a.m.

If you'd rather go for the overkill solution you can always cut out a couple chunks of the floor, dig down and out and pour footings.

RX8driver
RX8driver New Reader
10/3/15 8:44 a.m.

In reply to Kenny_McCormic:

In other words, doing it the right way.

Kenny_McCormic
Kenny_McCormic UltimaDork
10/3/15 2:14 p.m.

In reply to RX8driver:

Yeah, I do trust the engineering behind such and such slab being good enough, but gut feeling still says there should be a lot more concrete under such a thing.

Scottah
Scottah Dork
10/3/15 6:59 p.m.
KyAllroad wrote: Core drill a non critical spot. Take core sample to geotechnical lab for destructive testing. They'll crush it and figure out the strength for you. Generally concrete is speced to be 3,500 psi but since no supplier wants to have to replace substandard material they generally err on the side of stronger. When I tested concrete in the late '90s for a living 3,500 mix would test out around 4,000-4,300 at 28 days. YMMV

This.